jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
You ma omit If the conductors enter from the dome. But when the conductors enter through the box then you still count the EGC of the NM cable.
:happyyes:
You ma omit If the conductors enter from the dome. But when the conductors enter through the box then you still count the EGC of the NM cable.
echnically the canopy has to be labeled with the cu.in in order to use it. That seems silly , IMO esp, in the case of using a 12/2 vs a 14/2.
That's what I thought but I don't see that in Jumpers post. In 30 + years I have never seen a canopy labeled with the cu in amount so I just disregard that.
Using an unmarked canopy as per the exception is allowed for fixture wires that enter from the canopy or a domed fixture. If the fixture wires entered from the box they would have to be counted and if one wanted to use the canopy for extra fill space the canopy would need to be marked.
At least that is how I read it.
...And by the manufacturer.
(A) Box Volume Calculations. The volume of a wiring
enclosure (box) shall be the total volume of the assembled
sections and, where used, the space provided by plaster
rings, domed covers, extension rings, and so forth, that are
marked with their volume or are made from boxes the dimensions
of which are listed in Table 314.16(A).
The point was made that the article does not mention marked by the manufacturer but, IMO it is implied and How I would call it.
I don't believe you are correct. Please see post #17 and what (A)(2) says.
You could argue that the canopy is a box extension and not a box subject to (A)(2).
I don't believe you are correct. Please see post #17 and what (A)(2) says.
They don't go inside the fixture box. They mount in the fan canopy so don't effect the box fill.
That would be the 4" version. So the 3.5" ones are never compliant I guess - 4 Cu in.
I can't tell you how many older installs I have seen with 3 or 4 NM cables entering one of those boxes.Would have been with older 2 wire NM or if the raceway is an EGC.
I just want to know if anyone has had an inspector make a note of a pancake box and then had them request removal of the canopy to check for cu in marking at final.:?
Assuming the inspector asks at all, wouldn't he/she be more likely to make that request at the rough-in?
The canopy of the fixture generally isn't there at rough in.