Pancake box capacity

Status
Not open for further replies.

jumper

Senior Member
echnically the canopy has to be labeled with the cu.in in order to use it. That seems silly , IMO esp, in the case of using a 12/2 vs a 14/2.

That's what I thought but I don't see that in Jumpers post. In 30 + years I have never seen a canopy labeled with the cu in amount so I just disregard that.

Using an unmarked canopy as per the exception is allowed for fixture wires that enter from the canopy or a domed fixture. If the fixture wires entered from the box they would have to be counted and if one wanted to use the canopy for extra fill space the canopy would need to be marked.

At least that is how I read it.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Using an unmarked canopy as per the exception is allowed for fixture wires that enter from the canopy or a domed fixture. If the fixture wires entered from the box they would have to be counted and if one wanted to use the canopy for extra fill space the canopy would need to be marked.

At least that is how I read it.

...And by the manufacturer.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
...And by the manufacturer.

The point was made that the article does not mention marked by the manufacturer but, IMO it is implied and How I would call it.

(A) Box Volume Calculations. The volume of a wiring
enclosure (box) shall be the total volume of the assembled
sections and, where used, the space provided by plaster
rings, domed covers, extension rings, and so forth, that are
marked with their volume or are made from boxes the dimensions
of which are listed in Table 314.16(A).
 

luckylerado

Senior Member
FWIW, the code does seem capable of differentiating between field marked and factory marked when they mean to. I base this mainly on the language of 110.16 but both terms appear together in several places throughout the code. IMO it is or it is not, we should take it for what it says and give the author the benefit of the doubt that they knew what they were stating and not stating. Since the term "marked" is not defined, it could be taken both ways unless qualified with "field" or "factory"

I also see the code as drawing a clear line between "boxes" and "domed canopies" and therefore would not apply 314.16(A)(2) to a domed cover as it is not a box or the tittle of this paragraph would be "other boxes and domed covers".

JMO but I like to stir the pot:lol:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't believe you are correct. Please see post #17 and what (A)(2) says.


You don't believe I am correct yet you agree with me that the manufacturer should mark it...:? :lol:

I also don't think A(2) has anything to do with canopies. Canopies are not mentioned there just boxes-- different animal. Now because the manufacturer requirement is mentioned in A(2) should we infer the same for (A) or did the code panel deliberately leave it out in (A). Again, I think the manufacturer marking is req. as it would be beyond most of us to try and calculate the volume of some canopies and we certainly can make it whatever we wanted...LOL It would be silly to expect the installer to mark the canopy.

That being said I have never seen a canopy with the volume written on it.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I just want to know if anyone has had an inspector make a note of a pancake box and then had them request removal of the canopy to check for cu in marking at final.:?

Assuming the inspector asks at all, wouldn't he/she be more likely to make that request at the rough-in?
 