frizbeedog

Senior Member
Location
Oregon
A circuit exits a panel.

It enters a junction box adjacent to the panel. (behind the panel actually, on the other side of the wall).

It gets routed through a contactor.

It re-enters the panel and then exits the panel through a conduit, and out to the load.

I ask because I saw this last week and am looking for code refrences, for or against. Or similar examples.

Here's a picture of the install. You may notice it from a thread I did last week.

View attachment 1933
 
It's perfectly legal, see 312.8

The picture is not really relevant to the question though.

Roger
 
roger said:
It's perfectly legal, see 312.8

The picture is not really relevant to the question though.

Roger

Thanks roger. :) for the code reference.

The picture is not relevant to the question?

...it was, I thought, to represent whether or not that install was a violation.

An opinoin was given to me that this was a violation, from a co-worker, as an example of it being used as a raceway, and I wanted to clear it up.

...any violations regarding the installation as I described?

edit.
The picture just shows where the conductors are routed through before re-entering the panel, and then exiting it again. I see where you might be confused as to it's relevence.
 
Last edited:
The reason I said the picture is not relevant to the question is, it wouldn't matter what would be feeding in and out of the panel, substitute a photo cell for the contactors for instance, in either case it is a legal installation if 312.8 (splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space) is not violated.

Roger
 
roger said:
The reason I said the picture is not relevant to the question is, it wouldn't matter what would be feeding in and out of the panel, substitute a photo cell for the contactors for instance, in either case it is a legal installation if 312.8 (splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space) is not violated.

Roger

I gotcha now.

Somehow I knew it was right. Thanks.

:smile:
 
That looks like a perfectly acceptable way to add contactors for appliances or blowers for a fire-suppression hood system to me. I'm going to be adding three to a system on Monday.

Added: I probably would have used a single box for both contactors, though.

The 'other' electrician didn't know what we was doing. He ran two conduits directly into the microswitch box of the suppression head; no J-box. Nothing works correctly. He was quickly fired.
 
Last edited:
LarryFine said:
That looks like a perfectly acceptable way to add contactors for appliances or blowers for a fire-suppression hood system to me. I'm going to be adding three to a system on Monday.

That's exactly what I have to do. Add one for the deep fryer. :smile:
 