fifty five
came across a used 600 v. panelboard someone installed on a 240v service does anyone have a code ref.handy on something like this.
ya i agree panelboard will handle 240 stuff, but when you see all the high voltage brks. at first glance you're thinking 277/480. so it's misleading. just ask the guy who was selling property.
What is there to reference? It would be different if it were 240v rated equipment on 600v.
Sometimes you have to do that to get breakers with a high enough AIC for the available fault current.
Yes, I've installed 480VAC panels/breakers several times for that reason. In this photo of a 208 volt panel you can see that the CB will give you 65K at 120 volts.
This would usually be my preference - install a 'standard' offer instead of a special order one.But yes I have installed 600 volt panels for 208 systems per specification.
If someone is confused by the manufacturer's nameplate of a panel, I wonder what happens when they get to the nameplate of a dual voltage motor?:?