Getting conflicting information from multiple inspectors on proper clearance of water lines or drain lines above main pane what’s correct clearance
The large 12 story hospital that I retired from with over 50 electrical rooms that usually had at least three panels in each old rooms and of course plumbing water &/or drain lines. They had a shop make stainless steel three sided troughs that had a pitch to one end and at least a 1" copper drain line to the floor in case of a leak. Seemed like if they were installing additional circuit breaker panels they would relocate hot & cold water lines. Maybe the Local inspector will allow that .Know they had several such SS troughs over 480 volt normal & emergency supplied panels & safety switches. They were smart enough to to have a sloping piece of SS a foot above VFD'S that had pipes from a few feet to even 20' above them.Getting conflicting information from multiple inspectors on proper clearance of water lines or drain lines above main pane what’s correct clearance