hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 240/120V single phase 200amps Square D panelboard. The panelboard schedule shows 150A feeder breaker that takes up four space but it’s 2 poles.
The reason given is that unless a panel is ordered with subfeed breakers greater than 125 amps, or 150 amps, depending on the manufacturer, to fit a larger breaker, in this case a 150 amp breaker in an existing Square D panel, most manufacturer frame sizes will not fit into a standard “two pole” breaker frame size and requires a four pole frame size.
Would above be not in compliance with any NEC 2014 code section?
The reason given is that unless a panel is ordered with subfeed breakers greater than 125 amps, or 150 amps, depending on the manufacturer, to fit a larger breaker, in this case a 150 amp breaker in an existing Square D panel, most manufacturer frame sizes will not fit into a standard “two pole” breaker frame size and requires a four pole frame size.
Would above be not in compliance with any NEC 2014 code section?