I have calculated a panel but i am confused as how to calculate VA per circuit. All loads are continuous. My question is:
If I have 5 fluorescent fixtures in a circuit and they are 108W, the load per fixture would be 0.9Amps at 120V. right? 108W/120V= 0.9Amps
Now Total load for this circuit = 0.9 X 10 Fixtures = 9 Amps X 125% = 11.25 Amps
Everything is fine. But what number do I use to calculate VA on the panel?
The 9Amps value or 11.25Amps value? I am very confused about this. I think is 9Amps since the 125% is just for circuit and breaker calculation. Can someone explain if I am correct?
Thanks
My last question is. Once I have all this VA per circuits the process to find total Amps would be to devide total VA/240. In this case the service is 120/240 single phase? Explain please.