tonype
Senior Member
- Location
- New Jersey
312.3 Position in Wall.
In walls of concrete, tile, or other noncombustible material, cabinets shall be installed so that the front edge of the cabinet is not set back of the finished surface more than 6 mm (? in.). In walls constructed of wood or other combustible material, cabinets shall be flush with the finished surface or project therefrom.
Is the setback more than 1/4"?
If it is not a combustible service then 1/4" . I got hit on a receptacle box that was flush with the sheetrock but the tile guys came and added about 1/2". I don't see the problem with tile but code is 1/4"I did not measure it - very close though
Are there MWBCs in that panel with those breakers?
Hard to count the neutrals, but,,,,,,,,,,,,,,,,
I swear I see a MWBC with both conductors connected to one phase. Maybe it's just the camera angle
Yeah it looks like the blacks for the MWBCs are on the right, and one breaker up (same phase) that's a fire just waiting to happen.
It is a little odd to see a single phase panel with this low of a number of spaces that does not have an even number of connections for each bus. There should be 4 poles for A phase and only 2 poles for B phase in this panel.
It's a CH BR 6/12 panel. Odd arrangement but they still sell it.
Ah no.
So wannabee MWBCs with both hots on the same phase are not a fire hazard?
Notice I called it a "WANNABEE" MWBC.
And I don't know haw you can be sure where those blacks are going without a better picture
Are you sure you're a German?
Does a cover have to have intimate contact with a panel? Or are the screws sufficient. Photo below shows gypsum/spackle layer between the 2. View attachment 6345
It is a MWBC. One of the blacks goes almost to the bottom of the panel and loops back up to the bottom breaker of the center twin on the right. The other black follows the red down and across the bottom of the panel and lands on the center breaker on the left side.