Panel fed from adjacent building

Status
Not open for further replies.

reko19

Member
Is it OK to have one of the panels inside Building #1 fed from the UPS located in adjacent Building #2. My concern is that when service inside Building #1 is de-energized this particular panel would stay energized. Can't seem to find anything in NEC that relates to this installation. Perhaps installing a warning sign that the panel is fed from a different source would help?

Any help is appreciated.
 
Right on. Looks like not an issue, it is allowed under 225.30(A)(4 or 6). We will provide identification as required by 225.37. Thank you for your help.
 
Right on. Looks like not an issue, it is allowed under 225.30(A)(4 or 6). We will provide identification as required by 225.37. Thank you for your help.

Your very welcome.

I agree that this feed would be allowed in accordance with 225.30(A)(4).

Chris
 