Am i doing this correct,if i had a 3 phase 480 volt lighting panel with 50 kva connected loads of 277 volt lighting, continuous duty and i want to find out what size feeder i needer for thsi panel.  50kva x 1000=50000va, 
50000va/480v=104.16666/1.732=60.142413 x 1.25= 76 amp
So i would need #4 copper for this installation?
So even though you have single phase loads in the panel you calculate the feeder as a three phase load?
	
		
			
		
		
	
				
			50000va/480v=104.16666/1.732=60.142413 x 1.25= 76 amp
So i would need #4 copper for this installation?
So even though you have single phase loads in the panel you calculate the feeder as a three phase load?
 
				
 
 
		 
 
		