the bar is always short, how many equipment grounds can you stick in the bar?
S smilne New member Sep 17, 2004 #1 the bar is always short, how many equipment grounds can you stick in the bar?
hbiss EC, Westchester, New York NEC: 2014 Location Hawthorne, New York NEC: 2014 Occupation EC Sep 17, 2004 #2 Re: panel grounding bars One per hole unless the panel instructions say otherwise. If the bar isn't long enough use a longer one or add another. -Hal
Re: panel grounding bars One per hole unless the panel instructions say otherwise. If the bar isn't long enough use a longer one or add another. -Hal
H hurk27 Senior Member Location Portage, Indiana NEC: 2008 Sep 18, 2004 #3 Re: panel grounding bars Read the label on the panel cover most panels will allow 1 to 3 EGC's per terminal. And usually that's 14 through 10.
Re: panel grounding bars Read the label on the panel cover most panels will allow 1 to 3 EGC's per terminal. And usually that's 14 through 10.
S speedypetey Senior Member Location Hudson Valley, NY Sep 19, 2004 #4 Re: panel grounding bars Wayne is correct in my experience. One point to make is that conductors sharing a hole must be the same size. Neutrals are always one to a hole.
Re: panel grounding bars Wayne is correct in my experience. One point to make is that conductors sharing a hole must be the same size. Neutrals are always one to a hole.