Re: Panel height
It looks like a Code violation of Section 240.24(A). Looks like the center of the operating handles of the circuit breakers are more than 6 ft 7 in. above the floor. It would really be stretching section 240.24(A)(4), this would apply only to the overcurrent protection of "utilization equipment" at the upper level. A transfomer is not "utilization equipment".