I can't find that in the NEC. I know the working space and dedicated equipment space applies, but I never knew a panel has to be "readily accessible". I looked under both 408 and 240 and still didn't find that.Posted by Tom Baker: Panels are required to be readily accessible
E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (61/2 ft).