Re: panel location
As long as it's not in a prohibited location (clothes closet or bathroom) and there's enough working space, any location that suits you is fine. Realistically, the meter location often dictates panel location, and meter location is often dictated by POCO transformer location. The meter is on the end of the house closest to the padmount or pole mount transformer. The panel is generally immediately inside the house from the meter, be that in the basement right under the meter, in the garage back to back with the meter, or in another room but immediately near the meter. If the meter location does not "match up" with a suitable panel location, you normally have to mount a weatherproof main disconnect/overcurrect device outdoors and subfeed the main panel at a location in the house that suits you better. It would be quite normal for the prints or the builder to specify the panel location, then it's up to the electrician to accomodate that by whatever means necessary to meet code. In some geographic regions, it is normal to mount a weatherproof panel adjacent to (or in combination with) the meter and have all the branch circuit breakers in the panel outdoors.