So I finally had the chance to repair this mess and what I found is this ;
1)Sq D Homeline panel with contactor installed in it, 110.3 (B)
2) 20/20 quad breaker has two 240 volt loads connected to it and only one has a common trip handle tie, 225.33(B)
3) 12-2 NM in lower right of panel has no box connector on ,
4) 12-2 running to contactor has only single conductor being used, neutral for this contactor is connected to buss , 300.3(B)
5) 4 or more NM cables entering box through one connector, 110.3(B)
6) 12x12 enclosure filled over 40% ,312.8
7) ground bar installed with sheet metal screws, 250.8
8) 11 ground wires under one lug, 110.3(B) & 408.41
9) ground lead cut off in 12-2 NM feeding contactor in panel , 300.3 (B) & ?
The 12-3 coming into the upper left in pic #2 has all 3 wires being used as incoming switch legs , I believe this is a violation of 300.3(B) also.
If there are any other issues you guys see or if I have called out something incorrectly please fill in the blanks for me. Thank you
[/IMG]
[/IMG][/QUOTE]
And just to be cute how about 110.12 :grin: