good eye. is it a violation to put plywood in a junction box?Is that a plywood backing?
good eye. is it a violation to put plywood in a junction box?
what fire? I don't see a fire in the junction box.I'm sure its fine. The enclosure will contain the fire.
110.27 refers to live parts. are insulated wires considered "live"? If that was the case then extension cords would be "live" parts.That is plywood, and I have no idea why its in there. From what I can tell, the only thing in that panel is some wires and wire nuts.
I feel like there should be something to keep just anyone (including kids) from just opening the front door and grabbing a handful of hot wires. I think 110.27 A supports this.
When it was a panelboard, the front could be opened, and it was still a deadfront enclosure. Now, anyone can open it and access the wiring.
Well, they are individual conductors, which normally need to be enclosed in a chapter 3 wiring method.110.27 refers to live parts. are insulated wires considered "live"?
I don't see anything that 110.27(A) would apply to. How is this different from a hinged cover junction box?That is plywood, and I have no idea why its in there. From what I can tell, the only thing in that panel is some wires and wire nuts.
I feel like there should be something to keep just anyone (including kids) from just opening the front door and grabbing a handful of hot wires. I think 110.27 A supports this.
When it was a panelboard, the front could be opened, and it was still a deadfront enclosure. Now, anyone can open it and access the wiring.
They can also be in an enclosure, like a junction box or panel board enclosure.Well, they are individual conductors, which normally need to be enclosed in a chapter 3 wiring method.
They extension cord has an extra outer protective covering, so its a cable.
I'm sure you are right. The plywood brought "telephone cabinets" back to mind... I've installed a few but I' didn't recall them having a panel schedule on the door. Strange combination.This looks like a standard offering from most panel board manufacturers. It was called a 'telephone cabinet' and was originally intended for phone splice blocks they were often used for almost any splice.
I am sure they are still available.
I'm sure you are right. The plywood brought "telephone cabinets" back to mind...
They used standard panelboard fronts, so a directory holder would have been likely.I'm sure you are right. The plywood brought "telephone cabinets" back to mind... I've installed a few but I' didn't recall them having a panel schedule on the door. Strange combination.
Still not the same thing as branch circuit wiring.They can also be in an enclosure, like a junction box or panel board enclosure.
Some extension cords have an extra outer covering, some do not. look at lamp cords. Just two conductors with the insulation melted together.
And articles 312 and 314 are in chapter 3 and cover this cabinet.Well, they are individual conductors, which normally need to be enclosed in a chapter 3 wiring method.
They extension cord has an extra outer protective covering, so its a cable.
And articles 312 and 314 are in chapter 3 and cover this cabinet.
Has already been mentioned, but there are general use enclosures that have hinged covers and open just as easily. If you don't want such easy access then put a lock on it, put a screw with a fender washer in the cover placed so that the door can't be opened, weld it shut..... whatever it takes.
I've usually done the screw with fender washer like I mentioned when I have eliminated a panelboard but kept the cabinet as a junction/pull box.