C consultant New member Sep 25, 2004 #1 While helping a friend I noticed that his panel had the neutrals & grounds terminated on the same terminal strip. The installation was made circa 1960. IS THIS LEGAL?
While helping a friend I noticed that his panel had the neutrals & grounds terminated on the same terminal strip. The installation was made circa 1960. IS THIS LEGAL?
iwire Moderator Staff member Location Massachusetts Sep 25, 2004 #2 Re: Panel Neutral & ground terminations It can be. Does this panel also enclose the Service Disconnect?
Re: Panel Neutral & ground terminations It can be. Does this panel also enclose the Service Disconnect?
B bphgravity Senior Member Location Florida Sep 25, 2004 #3 Re: Panel Neutral & ground terminations See Section 408.20 of the NEC 2002.
iwire Moderator Staff member Location Massachusetts Sep 25, 2004 #4 Re: Panel Neutral & ground terminations Originally posted by bphgravity: See Section 408.20 of the NEC 2002. Click to expand... Bryan as you know the NEC is not retroactive. I would be very surprised if 408.20 was in the NEC circa 1960.
Re: Panel Neutral & ground terminations Originally posted by bphgravity: See Section 408.20 of the NEC 2002. Click to expand... Bryan as you know the NEC is not retroactive. I would be very surprised if 408.20 was in the NEC circa 1960.