brother said:Maybe i miss used the word 'main' in this context. Im talking about a breaker in panel 'A" that would feed panel 'B"
I understand that. :smile:
In that case you could work in panel B without PPE.
But the line side of the breaker in Panel A will still be hot so the PPE rules would still be required ..... in my opinion.
So what I am saying is that a panel with a main breaker in the same enclosure as the panel never relieves you of the hot work rules, you would have to shut off the feeder back at the source.
I can see your point about it being a poor design in a hospital situation as shutting off 84 or 126 circuits at any time of day will be more difficult then 'just' 42 circuits.
But still it comes down to money, less main breakers = less cost at the time of construction, I agree with you in the long run it may end up costing more.
For what it's worth the CEC (Canadian Electric Code) requires the line side of the service disconnect to still be totally enclosed when you open the normal panel cover. I am not sure if this only applies to dwelling units or service panels.
Nice rule in my opinion, means you can shut off the main in a residential panel and be entirely guarded from live parts. For me dealing with bare grounds in a live dwelling unit panel always made me nervous.