Hi-
I had a friend who sold there house,they had an independant inspection-and the inspector told the owner they had to replace the FPE-brk panels in the house.
I went to look @ the job-there is a 200 mcb panel in the basement,and a 30crt sub panel in the house-I could not find a GES for the main panel.The sub panel had a 3-wire feeder installed from the main panel.When I opened the sub it had no EG inside-just GC and hot legs for the branch circuits-the original install has the bond strap connect from the neutral to case-my question is-should this strap be installed?(250-32 (b)exception-# 1)and is it because there is no EGC present?
The owner also has a detached gararge-with a 3-wire feeder-and a 6-crt panel existing-with no GES,I know this is a recurring question-this panel should have a GES installed and keep the EGC and GC seperate?-again the original install has the bond strap installed,this house is considered an antique-built in the late 1700;s-thanks.
I had a friend who sold there house,they had an independant inspection-and the inspector told the owner they had to replace the FPE-brk panels in the house.
I went to look @ the job-there is a 200 mcb panel in the basement,and a 30crt sub panel in the house-I could not find a GES for the main panel.The sub panel had a 3-wire feeder installed from the main panel.When I opened the sub it had no EG inside-just GC and hot legs for the branch circuits-the original install has the bond strap connect from the neutral to case-my question is-should this strap be installed?(250-32 (b)exception-# 1)and is it because there is no EGC present?
The owner also has a detached gararge-with a 3-wire feeder-and a 6-crt panel existing-with no GES,I know this is a recurring question-this panel should have a GES installed and keep the EGC and GC seperate?-again the original install has the bond strap installed,this house is considered an antique-built in the late 1700;s-thanks.