Panel schedule add in amps

Status
Not open for further replies.

WA_Sparky

Electrical Engineer
Location
Vancouver, WA, Clark
Occupation
Electrical Engineer
I personally dislike this panel schedule layout completely. 2 separate columns for phase totals, amps per phase rather than VA or KVA, Amp totals not shown at the bottom, no demand factors shown.

Did anyone catch circuit 29,31? 25A/phase on a 20A breaker.
 

WA_Sparky

Electrical Engineer
Location
Vancouver, WA, Clark
Occupation
Electrical Engineer
So after all of that the original calculation (total 1Ø amps*120) is correct?
If you consider that a correct form to present data in...
All of the original phase amps are with respect to 120V...
A=103A+217A=320A @120V
B=69.2A+282.9A=352.1A @120V
C=74.7+263.2A= 337.9A @120V
Total amps = 1010A @120V

KVA = 121.2 KVA
Total Amps connected (@208V 3Ø): 121.2KVA*1000/208/1.732=336.43A
Total Demand Load Amps (@208V 3Ø, assuming they assigned demand factors properly): 79KVA*1000/208/1.732=219.29A
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
If you consider that a correct form to present data in...
All of the original phase amps are with respect to 120V...
A=103A+217A=320A @120V
B=69.2A+282.9A=352.1A @120V
C=74.7+263.2A= 337.9A @120V
Total amps = 1010A @120V

KVA = 121.2 KVA
Total Amps connected (@208V 3Ø): 121.2KVA*1000/208/1.732=336.43A
Total Demand Load Amps (@208V 3Ø, assuming they assigned demand factors properly): 79KVA*1000/208/1.732=219.29A

Phase currents dont add in three phase


Sent from my iPhone using Tapatalk
 
Status
Not open for further replies.
Top