Hello,
I have worked mostly with 120VAC panels, and this is the first time that I will be working with 120 and 208 VAC in the same panel.
The devices that I need to work with are 5 chargers, a controller and 3 workstations.
The chargers are going to be fed with 208VAC, they have a max current of 15A (L-L) each.
The controller is going to be fed with 120VAC, with a max current of 8A (L-N).
The workstations are going to be fed with 120VAC, with a max current of 4A (L-N) each.
As for the chargers, that are going to be fed with 208VAC L-L, the current has to be taken into account for each line ? Below I left the panel distribution:
If this is true, then the FLA of this distribution would be 167A, so a 200A panel would be good to go ?
Thank you in advance.
I have worked mostly with 120VAC panels, and this is the first time that I will be working with 120 and 208 VAC in the same panel.
The devices that I need to work with are 5 chargers, a controller and 3 workstations.
The chargers are going to be fed with 208VAC, they have a max current of 15A (L-L) each.
The controller is going to be fed with 120VAC, with a max current of 8A (L-N).
The workstations are going to be fed with 120VAC, with a max current of 4A (L-N) each.
As for the chargers, that are going to be fed with 208VAC L-L, the current has to be taken into account for each line ? Below I left the panel distribution:
A | B | C | |
WS1 | 4 | ||
WS2 | 4 | ||
WS3 | 4 | ||
CONTROLLER | 8 | ||
CHARGER 1 | 15 | 15 | |
CHARGER 2 | 15 | 15 | |
CHARGER 3 | 15 | 15 | |
CHARGER 4 | 15 | 15 | |
CHARGER 5 | 15 | 15 | |
TOTAL | 57 | 64 | 49 |
If this is true, then the FLA of this distribution would be 167A, so a 200A panel would be good to go ?
Thank you in advance.