I am looking for some help in sizing a panelboard that will be supplying 30 120 volt 2000 watt lights. The voltage is 120/208 3 phase. 60,000 watts/208x1.732= 167 amps. It has been so long since I have had to calculate this stuff, this has really woke me up to how much i have forgotten. The lights will all be operating at the same time but probably not for 3 hrs so do I add the 125% for continious load. Also as bad as it sounds i am not sure if the above 167 amp demand was figured correctly. I do know tonight the study books come back out. Thanks for any help!