I have a few code questions. I remove a flush-mount residential panel exterior stucco and replace it with a surface-mount panel that covers the entire cavity.  I installed the Romex cables from the old panel with Romex BX connectors coming in from the back of the new panel. The inspector is calling out the conductors coming from the rear of the panel? and wants the BX connectors to be water-tight. The panel is outdoor-rated, and the knockouts are in the back of this panel. Can you assist with the code requirements?  
FYI, the side of the house where it's installed has an overhang; there is no way water will ever come up 5 plus feet to flood the panel. A little stumped?
	
		
			
		
		
	
				