Panel wiring - which thread?

Status
Not open for further replies.

KentAT

Senior Member
Location
Northeastern PA
I recall a recent post that mentioned a certain conductor type that was not approved for use, I think by UL. It might have been related to wiring in a control panel.

I have searched quite a bit, but I cannot find it.

Anyone remember what I'm talking about? Maybe MTW, MW, or similar?:confused:

Kent
 
If you are talking about control panels, UL508a is fairly specific that only certain types of wire are acceptable.

29.2 Conductor requirements
29.2.1 All internal wiring of power circuits shall have a temperature rating of 90?C (194?F) minimum and shall be one of the following:
a) Machine tool wire that complies with the Standard for Machine-Tool Wire and Cables, UL 1063. Flexing or Class K type machine tool wires and cables shall be installed in accordance
with 29.3.11;
b) Thermoset insulated wire that complies with the Standard for Thermoset-Insulated Wires and Cables, UL 44;
c) Thermoplastic insulated wire that complies with the Standard for Thermoplastic-Insulated Wires and Cables, UL 83;
d) Appliance wiring material that complies with the Standard for Appliance Wiring Material, UL 758; or
e) Welding cable installed in accordance with 29.3.11.
 