Panel with cardboard or wood to protect wire from edges in panel

Status
Not open for further replies.

MPdesign

Member
Location
USA
I have a few commercial panels with cardboard and wood left in the panels where there are bars or edges to protect the cable.

What is the code section that disallows this - and what should be done instead?

Thank you! :happyyes:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Not sure there is a rule against having wood in a panel. Personally, I don't like it but I can't find an article that would disallow it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is as close as you may get if the circuit breaker is considered a device that produces arcs.

110.18 Arcing Parts. Parts of electrical equipment that in ordinary operation produce arcs, sparks, flames, or molten
metal shall be enclosed or separated and isolated from all
combustible material.
 

RumRunner

Senior Member
Location
SCV Ca, USA
Occupation
Retired EE
I have a few commercial panels with cardboard and wood left in the panels where there are bars or edges to protect the cable.

What is the code section that disallows this - and what should be done instead?

Thank you! :happyyes:

There are products made especially for this. Some are made of porcelain to support cables in man hole.
Since your application is inside panels, there is an outfit whose address escapes me that manufacture cable cleats made of silicone polymer. If you don't require custom shaped cleats you can use those with fluted side to provide a nest for the cables.
Google cable insulating cleats.
Good luck
 

JFletcher

Senior Member
Location
Williamsburg, VA
I have a few commercial panels with cardboard and wood left in the panels where there are bars or edges to protect the cable.

What is the code section that disallows this - and what should be done instead?

Thank you! :happyyes:

I've seen one hotel recently with 40 yr old FPE panels with wooden stakes bolted to the outside to act as wire gutters for tons of NM... ugliest thing I think Ive ever seen... funny thing is the feeders to the same panels are in RMC and a pretty huge wire gutter (10x10", maybe larger).

eta: not a NM staple anywhere to be seen....not sure when that was code but Ive seen older installs stapled within 2' of the panel... yes, I have pictures. :roll:
 

MPdesign

Member
Location
USA
After thinking about this a bit, I think that Mason Pads (3/8" thick and cuts with scissors) from Grainger would be good. link
51TLgA8ZNQL.jpg

or possibly a Ditra Mat which is actually the orange mat that goes under tile that you can get at Lowes or Home Despot. link
ditra-schluter-uncoupling_membrane.jpg

Thank you all for your input!
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
There is no Code restriction on wood, in fact wood mounting panels is often something used in certain applications (albeit I've never seen it in CB panelboards). Wood is also used in large incoming terminal compartments to lace and brace the cables. Cardboard in any capacity however is something I have seen rejected by AHJs on several occasions, even as a temporary work cover during construction. Besides, it's a terrible solution for permanent abrasion protection because it will break down fairly fast.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Well that make sense, but melting copper or aluminum could be hazardous also, so it is prolly best to not install any conductors in electrical equipment just to be on the safe side.:)

Which dovetails nicely with another common question; "If I punch a conduit hole in my enclosure, don't I violate the UL listing?"

No conductors, no conduit needed, so no holes, everything is good!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is insulated wire actually combustible? There is a difference between combustible and will burn under certain conditions.
By some definitions the insulation is not combustible as they require the product be easily ignitable.

The International Fire Code says this "Combustible materials are natural or synthetic materials that can be ignited and support combustion." By that definition the insulation is combustible. This definition leaves out the "easily" part.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Here are some useful :) definitions from the NFPA glossary of terms.

Combustible Capable of reacting with oxygen and burning if ignited. [listed more then once]

Combustible A combustible material is any material that, in the form in
which it is used and under the conditions anticipated, will
ignite and burn or will add appreciable heat to an ambient
fire.

Combustible Capable of undergoing combustion. [This one is listed > ten times]

Combustible Capable of burning, generally in air under normal conditions
of ambient temperature and pressure, unless otherwise
specified. Combustion can occur in cases where an oxidizer
other than oxygen in air is present (e.g., chlorine, fluorine, or
chemicals containing oxygen in their structure).

Combustible A substance that will burn.

Combustible Capable of burning, generally in air under normal conditions
of ambient temperature and pressure, unless otherwise
specified; combustion can occur in cases where an oxidizer
other than the oxygen in air is present (e.g., chlorine,
fluorine, or chemicals containing oxygen in their structure).

Combustible A material or structure that will release heat energy on
burning.

Combustible (Material) A material that, in the form in which it is used and under the
conditions anticipated, will ignite and burn; a material that
does not meet the definition of noncombustible or limited combustible. [listed six times - actually maybe the most useful of the bunch]

Combustion A chemical process of oxidation that occurs at a rate fast
enough to produce heat and usually light in the form of
either a glow or flame. [they seem to have gotten this one right at least]
 

Besoeker

Senior Member
Location
UK
There is no Code restriction on wood, in fact wood mounting panels is often something used in certain applications (albeit I've never seen it in CB panelboards). Wood is also used in large incoming terminal compartments to lace and brace the cables. Cardboard in any capacity however is something I have seen rejected by AHJs on several occasions, even as a temporary work cover during construction. Besides, it's a terrible solution for permanent abrasion protection because it will break down fairly fast.
I've seen a few older installs where cable clamps were made from treated plywood.
 

just the cowboy

Inactive, Email Never Verified
Location
newburgh,ny
Seen it for years

Seen it for years

It was quite common to find wood spacers in old industrial panels, with the latches on the cover that turned 90 deg to close. They would be there to hold the wires away from the clamp part. I have seen more than one wire clamped to the cover = boom.
 