Hello All,
I am a fairly young Electrical Engineer whose currently working with a client to update/ clean up some of their site construction specifications.
I am currently working on their Panelboard section. One requirement that they have in the specification is a current density of 1000A/sq-in for bus bars. I think this is a bit of a "legacy" requirement as my counterparts on the client side don't know why it is required. I have looked at UL67 and NEMA PB1 and all I see is a requirement for bus bars to pass temperature rise testing. My gut is telling me that this requirement can be removed from the specification, and as long as future Panelboards have buses that are sized per UL67, we should be good.
Does anyone have any experience or insight as to why such a requirement could be in this specification?
I am a fairly young Electrical Engineer whose currently working with a client to update/ clean up some of their site construction specifications.
I am currently working on their Panelboard section. One requirement that they have in the specification is a current density of 1000A/sq-in for bus bars. I think this is a bit of a "legacy" requirement as my counterparts on the client side don't know why it is required. I have looked at UL67 and NEMA PB1 and all I see is a requirement for bus bars to pass temperature rise testing. My gut is telling me that this requirement can be removed from the specification, and as long as future Panelboards have buses that are sized per UL67, we should be good.
Does anyone have any experience or insight as to why such a requirement could be in this specification?