Assuming I have the required clearance for a 225A 208V 3 phase panelboard in a "storage room", Is this permitted or not ???? Can't find anything in the NEC not allowing it.
The working clearance required by article 110 takes up all the "storage" space. You need 30"Wx36"D and that space may not be used for storage. See 110.26(B).