PanelBoard Location

Status
Not open for further replies.

blues

Member
Location
Nevada
Please see the attached PDF. I am I allowed to used the closed door for my 30" horizontal required working space.
 

Attachments

  • Panel Location.pdf
    48.9 KB · Views: 1

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
As long as you have 30" with the door closed or open you are good. If the door was hinged opposite of what you are showing it would still be compliant, IMO
 

Marshmo

Member
Location
OK, USA
Occupation
Electrical Contractor
There will be a "T" framed in the panel wall where it intersects with the adjacent wall. Hopefully that's not in the way.
 