G guschash Senior Member Location Ohio Sep 24, 2020 #1 Where in the code does it say that panelboad can't be in a closet? I been searching but have not found it. I read 408 but didn't come across it.
Where in the code does it say that panelboad can't be in a closet? I been searching but have not found it. I read 408 but didn't come across it.
dkidd Senior Member Location here Occupation PE Sep 24, 2020 #2 240.24 (D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets. see https://forums.mikeholt.com/threads/panel-in-closet.2556288/#post-2611808
240.24 (D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets. see https://forums.mikeholt.com/threads/panel-in-closet.2556288/#post-2611808
Jraef Moderator, OTD Staff member Location San Francisco Bay Area, CA, USA Occupation Electrical Engineer Sep 24, 2020 #4 And... working space clearances will get in the way in a lot of cases. 110.26? I’m in my car, can’t access my code.
And... working space clearances will get in the way in a lot of cases. 110.26? I’m in my car, can’t access my code.
J jusme123 Senior Member Location NY Occupation JW Sep 24, 2020 #5 Jraef said: And... working space clearances will get in the way in a lot of cases. 110.26? I’m in my car, can’t access my code. Click to expand... I pictured you with a heads up display of MH site on windshield
Jraef said: And... working space clearances will get in the way in a lot of cases. 110.26? I’m in my car, can’t access my code. Click to expand... I pictured you with a heads up display of MH site on windshield