I am a new electrical engineer and I am having trouble finding literature on how to determine wire sizing.
How would I determine the wire size needed for a 120/208V Lighting Panel that is rated for 225A (estimated load is approx 200A) 3-phase 4wire. The run is 500ft and I assume I am aiming for less than 3% voltage drop. I don't know whether this run is on the primary or secondary side of the 480/120-208v transformer but I am again assuming secondary.
I would like to be able to do this by hand if possible because i have tried 4 websites and have recieved 4 different answers with the same data. Seems fishy. I have one website telling me 1000kcmil one telling me 350kcmil and another telling me 700kcmil. Any help would be appreciated.
Thank you.
How would I determine the wire size needed for a 120/208V Lighting Panel that is rated for 225A (estimated load is approx 200A) 3-phase 4wire. The run is 500ft and I assume I am aiming for less than 3% voltage drop. I don't know whether this run is on the primary or secondary side of the 480/120-208v transformer but I am again assuming secondary.