xformer
- Dallas, Tx
- Master Electrician
Is it permissible by code to install a MLO panelboard, without a disconnect,  to the secondary of a 480 primary / 208Y 120V secondary transformer?
			How do you intend to comply with 240.21(C) and 408.36?
By using a Delta-Delta transformer and labeling the primary OCPD as also the panel disc.
post 1 states 208Y/120 post 3 states delta which is it ??
( somewhat a mute point as it can change the Art 240 rules, won't change the 408.36 rule)
I am trying to understand the validity of M.L.O. panels.
I am unclear as to exactly what puzzles you about MLO panels.
I am trying to understand the validity of M.L.O. panels. I am familiar with the rules of Art 240 and 408.36. This is not an actual installation. Its more of just a brain storm.
The sticking point in your example is the upstream transformer. If a panel is fed from an ATS, it would be perfectly fine to be MLO, and in some cases mandatory.
I assume you mean on the 'mandatory' comment - I was pretty sure that hospital life safety and critical branch panels downstream from their respective ATS's were not allowed to have main breakers. But of course looking through Article 517 right now I can't seem to find it.can you elaborate
Edit: looks like I was mistaken - it doesn't appear to be in any codes or standards and just seems to be a good design practice.
I have half a mind to petition this to the NFPA 99 committee, though it should be mandatory for any emergency transfer switch.
Are MLO panels designed to be used in conjunction with the requirement of 408.36?
I have observed M.L.O. panels installed with conductor termination on the main lugs leaving me to just wondering where the requirements of 408.36 went...
An OCPD immediately after an ATS is a single point of failure can will compromise the reliability of the loads served by the ATS. In a hospital this can cause devastating outages - trust me I've seen it happen. I was the senior electrical engineer for a major healthcare system in Boston for many years and after one such outage we changed our design standards to eliminate these OCPDs where ever possible.I don't see a problem one way or the other, the feeder to the downstream panel will have OCP anyways even if it's before the ATS
As far as the need to make a proposal, why would a designer put a main breaker in a panelboard that doesn't require it?
As an aside, Isolation panelboards have mains even if supplied by the Critical Branch.
Roger
The OCP ahead of the ATS is the same thing and can create the same problem. The question is, why did the OCP open in the first place? Was it an overload or a fault? But, back to my earlier post, why would a designer want to put a main where one is not wanted or needed?An OCPD immediately after an ATS is a single point of failure can will compromise the reliability of the loads served by the ATS.