S sleepy Senior Member Sep 2, 2008 #1 i cannot find in the nec and i know its their about panelboard (cannot) being installed in bathrooms can i get some help thanks
i cannot find in the nec and i know its their about panelboard (cannot) being installed in bathrooms can i get some help thanks
R roger3829 Senior Member Location Torrington, CT Sep 2, 2008 #2 It is allowable. As long as it does not contain the service disconnect
raider1 Senior Member Staff member Location Logan, Utah Sep 2, 2008 #4 Take a look at 230.70(A)(2) for service disconnecting means being located in bathrooms. Also if this is a dwelling unit, overcurrent devices are not permitted to be installed in bathrooms, see 240.24(E). Chris
Take a look at 230.70(A)(2) for service disconnecting means being located in bathrooms. Also if this is a dwelling unit, overcurrent devices are not permitted to be installed in bathrooms, see 240.24(E). Chris
R rtr15077 Member Location North Carolina Sep 2, 2008 #5 Try 240.24(E). Can't have overcurrent protection in bathrooms.