Can you run wires from a 480v panel through an existing 208v panel if they are clearly identified and there is sufficiant space?
 
Re: panelboards

Originally posted by rickehle:
Can you run wires from a 480v panel through an existing 208v panel if they are clearly identified and there is sufficiant space?
Yes. Your major concerns would be the identification of the grounded conductors since the 208 v panel will have grounded conductors from 2 different systems and labelling of the panelboards to identify each system.