I appreciate the answers, and the attention to detail.
I understand all that: integrated EGC in trunk cable bonds micros, and rails to micros thru mounting bolts. Modules are bonded to rail thru mid-clamps on 99% of racking. Bonding splices. Etc.
Couldn't ti be argued that ac trunk cable only runs on RACKING? Not modules. Not sure if i buy this myself..... but hear me out here.
The micros do not touch m
odules.
Technically, the modules don't see more than 48 VDC.
The way I see it is the mod.s are maximum 48 VDC components.... bolted to...... a bonded and grounded metal rack and micro system at 240 VAC.
Why would I
not want to bond modules, especially since most mid-clamps already automatically bond modules to rails?
Because some inspectors want/demand
lay-in-lugs on module frames. I am fine with bonding mid-clamps. And i will always use them. But..... Lay in lugs......not a fan, given a choice.....been there, done that 10 yrs ago:rant: :thumbsdown:
And I nearly failed inspection even though everything was bonded..... but inspector wanted lay in lugs. I could just tell inspector, "modules don't even need bonding, but look here, I did it anyways by way of the bonding mid-clamps, b/c i am a swell guy ".