This reserved space permits busways, conduits, raceways, and cables to enter the equipment. The dedicated electrical space must be clear of piping, ducts, leak protection apparatus, or equipment foreign to the electrical installation. Plumbing, heating, ventilation, and air-conditioning piping, ducts, and equipment must be installed outside the width and depth zone.
Foreign systems installed directly above the dedicated space reserved for electrical equipment must include protective equipment that ensures that occurrences such as leaks, condensation, and even breaks do not damage the electrical equipment located below.
I don't understand this statement. Could you explain? I think you can always install a panel above or below another panel. You might have an interesting time with the conduit runs, but 110.26(F) would not enter into the picture. The "dedicated space" begins at the front of the panel, not at the wall.Originally posted by steve66: I wish there was an exception for adding panels to an existing space. To really comply with this section, I usually need a building addition to install a NQOD panel.
OK. I see it now (not having read closely enough he first timeOriginally posted by steve66: Charlie: We are talking about the dedicated space required above a panel, right? Not the working space in front of the panel. If the panel is aginst the wall, the equipment space would start at the wall.
110.26(A)(3) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 150 mm (6 in.) beyond the front of the electrical equipment.