I've been scratching my head on this one, being that I want to believe this is "ok", but I'm not seeing it. So I differ to the masses, and the masters.
We have a couple of chillers, each fed with parallel 500kcmil, fed from 1000a breakers. The chillers are 760a name plate, with an internal 800a breaker, that also happens to be the disconnect.
So to my question, can any one think of a way this is legal?
Art. 240.4 leads me to believe not, and I can't find any thing in Art. 440 to lead me to believe it's OK. I have no doubt the breaker size is ok, it's the wire size that is the problem.
Anybody?
Also, are these feeders? or branch circuits? :roll: I did some digging on the forum and couldn't finish reading an '06 thread on the topic, so I'll re-open the can of worms.
Thanks,
Doug S.:-?