Re: parallel arc vs series arc
One time the demo showered the room with a barrage of sparks. Another the guillotine 's blade got red hot. When they tried the same experiment with a cord that had a grounding conductor in it it worked just fine. What was funny is with the two conductor lamp cord a regular 15 amp single pole breaker cleared the fault faster with no damage to the cord or guillotine other than the small cut through the insulation. AFCI's will not trip on a parallel arc unless it reach's 75 amp's but a arc that migrates to grounding will trip on as little as 30 ma. This will not protect past the wall receptacle unless a ground fault is involved!
I have watched several of these rather embarrassing demo's and when they tried to guillotine a two conductor lamp cord the cord went up in smokeBy Harley you have not witness the CH demos or reviewed U.L. 1699 spec.