Coastalguy1
Member
- Location
- Virginia Beach, VA
I have a piece of equipment (HVAC) that is getting upgraded. The existing circuit is (3)#1/0 THHN cu,(1)#6 cu gnd in 1-1/4" EMT conduit.
My new equipment's MCA=165amps. If I parallel a (3) conductor 1/0 THHN cu w/gnd MC cable next to it I can achieve and meet the 165amps MCA for the new equipment. Choice for MC Cable vs. EMT is cost being it's a run across a building ceiling space. Voltage drop has been calculated.
My question is can I have a parallel feed with different raceway types?
My new equipment's MCA=165amps. If I parallel a (3) conductor 1/0 THHN cu w/gnd MC cable next to it I can achieve and meet the 165amps MCA for the new equipment. Choice for MC Cable vs. EMT is cost being it's a run across a building ceiling space. Voltage drop has been calculated.
My question is can I have a parallel feed with different raceway types?