The last thread on parallel conductors got me to thinking, are all the conductors required to be the same length or just in each raceway? Maybe thinking to much into this but hey thats how we learn.
310.4(C) Separate Cables or Raceways.
Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics. Conductors of one phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor shall not be required to have the same physical characteristics as those of another phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor to achieve balance.
Yes.For example if i have a 120/208V, 3 phase, 4 wire feeder can i have phase A and B copper and phase C aluminum (in same conduit)?
Yes.For example could phase A and B be fused differently than phase C?