Can al and copper conductors be used. For example. 1 hot copper and the second hot aluminum?
Sent from my LGLS770 using Tapatalk
Sent from my LGLS770 using Tapatalk
Can al and copper conductors be used. For example. 1 hot copper and the second hot aluminum?
Sent from my LGLS770 using Tapatalk
If both conductors of A phase are AL why would there be a problem?My buddy is studying for his masters and said he couldnt find where is says u cant have a phase paralleled 1 al and 1 al
Sent from my LGLS770 using Tapatalk
My buddy is studying for his masters and said he couldnt find where is says u cant have a phase paralleled 1 al and 1 al
Sent from my LGLS770 using Tapatalk
What are you asking? Can one paralleled conductor be Cu and one Al? No, not it they are on the same phase. Yes, if they are not.Can 1 be al and 1 cu
Sent from my LGLS770 using Tapatalk
Can 1 be al and 1 cu
Sent from my LGLS770 using Tapatalk
Thanks for all the replies.
Is there a instance where a being co and b being al would be used?