We are doing some big parallel feeders and I got to thinking about something hypothetical.
Say you have a 5000 amp feeder breaker and you decide, for whatever reason, to run 34 parallel sets of conductors with #1/0 ungrounded conductors in each of the 34 parallel PVC conduits.
250.122(F)(1)(b) says the EGC in each parallel conduit must be sized per table 250.122 based on the setting of the OCPD. 700kcmil copper EGC in this example.
However, 250.122(A) says the EGC shall not be required to be larger than the circuit conductors supplying the equipment.
Which one wins?
Logically, the (F)(1)(b) rule is there because the EGC must be able to carry enough current to make the breaker trip. But in my extreme example, if there is a phase to EGC fault INSIDE of one of the conduits (I’ve seen it happen), I wouldn’t think that a 1/0 conductor would potentially not carry enough to make a 5000a breaker trip. Yes, the fault current would flow in all of the phase conductors via the parallel connection point, but the same is true for the EGC.
Thoughts?
Say you have a 5000 amp feeder breaker and you decide, for whatever reason, to run 34 parallel sets of conductors with #1/0 ungrounded conductors in each of the 34 parallel PVC conduits.
250.122(F)(1)(b) says the EGC in each parallel conduit must be sized per table 250.122 based on the setting of the OCPD. 700kcmil copper EGC in this example.
However, 250.122(A) says the EGC shall not be required to be larger than the circuit conductors supplying the equipment.
Which one wins?
Logically, the (F)(1)(b) rule is there because the EGC must be able to carry enough current to make the breaker trip. But in my extreme example, if there is a phase to EGC fault INSIDE of one of the conduits (I’ve seen it happen), I wouldn’t think that a 1/0 conductor would potentially not carry enough to make a 5000a breaker trip. Yes, the fault current would flow in all of the phase conductors via the parallel connection point, but the same is true for the EGC.
Thoughts?