250.122(F)(1)(b) says the EGC in each parallel conduit must be sized per table 250.122 based on the setting of the OCPD. 700kcmil copper EGC in this example.
However, 250.122(A) says the EGC shall not be required to be larger than the circuit conductors supplying the equipment.