chevyx92
Senior Member
- Location
- VA BCH, VA
The way I read the code this is allowed although I have never seen it done before. I am now in a situation where I must achieve 3phase 480V 400A in (1) 4" Emt conduit. I would use 600 MCM CU but the boss says it costs too much and doesn't want to spend the money on it. So I propose to run (6) 300 AL and 1 ground in the conduit. We don't need a neutral as this is a sub-fed power panel and panel is loaded. (6) 300 AL would give me 408A ampacity which is what I need. My question is am I correct in only pulling the (1) ground in the conduit? The ungrounded conductors are parallelled and will be on a 400A breaker. I come up with a size of #1 AL based on table 250.122. Is this correct or do I need to parallel the ground as well??