parallel conductors

Status
Not open for further replies.

bosshoss

New member
when using parallel conductors do each of the conductors have to be able to carry the total load or are you allowed to use the parallel conductors as one ie.2 500s instead of 1 1000,if it is the first one what is the purpose of parallel conductors, also i need code references. THANKS
 

ron

Senior Member
Re: parallel conductors

Why else would you use parallel conductors if they wouldn't share the load? I'm sure the question has a catch that I am not seeing, but check the index of your code book under "conductors - paralleled" for 7 code references.
 

bennie

Esteemed Member
Re: parallel conductors

BossHoss: Parallel conductors 1/0 and larger, the ampacity adds.

Parallel conductors #1 and under, have the ampacity of one.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: parallel conductors

Bennie you should write code articles, short and to the point. :)

What Bennie said answers your question but 310.4 goes into all the details and provides other articles that must be applied like 250.122(F) and 310.15(B)(2)(a).

For large services (or loads) the use of parallel conductors is necessary, a 4000 amp service might have 10 sets of 600 kcmil.

This makes a nice pile of scrap when you remove it. :D
 