I just though I would share this experience.
I had a church that needed a new service due to damage from a garbage truck. I came in with a new 800Amp service. Since it was for a damaged service, I just replaced the main switch and everything upstream to the weather head. However, the physical size of the new switch did not allow my parallel conduits to enter both on the top or both on the bottom. I had to take one conduit out the top and one out the bottom. They both met at the LB's going outside, and ran neatly up the side of the building to the Head.
When the condutors got installed, due to the placements of the conduits and bending radius inside the switch, I was left with several different lengthed conductors sticking out of the 2 weather heads. I kept the parallels the same length, but they looked different lengths from the outside.
The Power Company came and CUT all the conductors to the same length. He said it was standard practice to cut all the conductors to same length. I told him that that is fine on single conductors, but these were parallel. We had to figure out which end came from which, and the cut off the same amount on a cut conductor's parallel. The one conductor ended up being only 6 inches long.
It took me a day to run these parallel runs myself, I did not want to do it again, but what is worse, is that if I had not noticed the cut ends laying on the ground, I would have had parallel conductors that truly weren't parallel, because all the current would have been on the shortest of the 2.
Just a 'heads up' when it comes to an installation like this. Yes I would have liked to make it a nice pretty installation, with all of my conductors the same length, but what I had to work with didn't allow for that.
I had a church that needed a new service due to damage from a garbage truck. I came in with a new 800Amp service. Since it was for a damaged service, I just replaced the main switch and everything upstream to the weather head. However, the physical size of the new switch did not allow my parallel conduits to enter both on the top or both on the bottom. I had to take one conduit out the top and one out the bottom. They both met at the LB's going outside, and ran neatly up the side of the building to the Head.
When the condutors got installed, due to the placements of the conduits and bending radius inside the switch, I was left with several different lengthed conductors sticking out of the 2 weather heads. I kept the parallels the same length, but they looked different lengths from the outside.
The Power Company came and CUT all the conductors to the same length. He said it was standard practice to cut all the conductors to same length. I told him that that is fine on single conductors, but these were parallel. We had to figure out which end came from which, and the cut off the same amount on a cut conductor's parallel. The one conductor ended up being only 6 inches long.
It took me a day to run these parallel runs myself, I did not want to do it again, but what is worse, is that if I had not noticed the cut ends laying on the ground, I would have had parallel conductors that truly weren't parallel, because all the current would have been on the shortest of the 2.
Just a 'heads up' when it comes to an installation like this. Yes I would have liked to make it a nice pretty installation, with all of my conductors the same length, but what I had to work with didn't allow for that.