is there any code provision allowing an EGC to be made up of parallel wires as opposed to a single wire?
Bob250.122(F) Conductors in Parallel. Where conductors are run in parallel in multiple raceways or cables as permitted in 310.4, the equipment grounding conductors, where used, shall be run in parallel in each raceway or cable. One of the methods in 250.122(F)(1) or (2) shall be used to ensure the equipment grounding conductors are protected.
(1) Each parallel equipment grounding conductor shall be sized on the basis of the ampere rating of the overcurrent device protecting the circuit conductors in the raceway or cable in accordance with Table 250.122.
(2) Where ground-fault protection of equipment is installed, each parallel equipment grounding conductor in a multiconductor cable shall be permitted to be sized in accordance with Table 250.122 on the basis of the trip rating of the ground-fault protection where the following conditions are met:
250.122 would seem to require GF protection for paralleled EGC that are smaller than what would normally be allowed for the OCPD size on the circuit.Originally posted by charlie:
Ryan, you didn't read far enough. This is found towards the end of 310.4:
"Where equipment grounding conductors are used with conductors in parallel, they shall comply with the requirements of this section except that they shall be sized in accordance with 250.122."
You owe me a beer the next time we meet.
Very good point!Originally posted by petersonra:Maybe it just doesn't come up that often since the EGC is usually quite a bit smaller anyway.
I agree. Since they went out of their way to explicitly state that it is OK to parallel some conductors, and then gave specific rules and exceptions under which this is acceptable, I believe they did imply that an EGC should not be on the list. Or so I infer.Originally posted by charlie: Don, I think the way the Code is worded, it is inferred.