Parallel EGC

Status
Not open for further replies.
Re: Parallel EGC

I do not see any way in to comply with Table 250.122 using parallel EGCs, there are no notes to the table explaining how to figure how many of one conductor equals another.

Even when running parallel EGCs with parallel feeders each EGC is large enough to be the sole EGC or GFP must be provided.

250.122(F) Conductors in Parallel. Where conductors are run in parallel in multiple raceways or cables as permitted in 310.4, the equipment grounding conductors, where used, shall be run in parallel in each raceway or cable. One of the methods in 250.122(F)(1) or (2) shall be used to ensure the equipment grounding conductors are protected.

(1) Each parallel equipment grounding conductor shall be sized on the basis of the ampere rating of the overcurrent device protecting the circuit conductors in the raceway or cable in accordance with Table 250.122.

(2) Where ground-fault protection of equipment is installed, each parallel equipment grounding conductor in a multiconductor cable shall be permitted to be sized in accordance with Table 250.122 on the basis of the trip rating of the ground-fault protection where the following conditions are met:
Bob
 
Re: Parallel EGC

sure as long as they are 1/0 or larger and they are with all of the phase conductors (like in a cable tray). If you have individual runs of conduit, it would not be practical since the grounding conductor has to be large enough for the overcurrent device and in each run. :D
 
Re: Parallel EGC

Ryan, you didn't read far enough. This is found towards the end of 310.4:

"Where equipment grounding conductors are used with conductors in parallel, they shall comply with the requirements of this section except that they shall be sized in accordance with 250.122."

You owe me a beer the next time we meet. :D
 
Re: Parallel EGC

Originally posted by charlie:
Ryan, you didn't read far enough. This is found towards the end of 310.4:

"Where equipment grounding conductors are used with conductors in parallel, they shall comply with the requirements of this section except that they shall be sized in accordance with 250.122."

You owe me a beer the next time we meet. :D
250.122 would seem to require GF protection for paralleled EGC that are smaller than what would normally be allowed for the OCPD size on the circuit.
 
Re: Parallel EGC

Charlie: Here in the office all I have is the handbook. I have the NEC in my truck, and at my home and on my home computer. I have a hard time with the handbook sometimes...you start reading the text, then skip the commentary, then read more text, then skip more commentray, then miss the last sentance of the text!

Alright, I'll buy you a beer next time we meet...I think it's my turn anyway :D
 
Re: Parallel EGC

Section 310.4 allows the use of parallel equipment grounding conductors provided each conductor is at least 1/0 or larger. The size of the parallel EGC is based on the cross-sectional of that required by Table 250.122. Example: feeder supplied from a 2000 amp breaker requires a 250 kcmil EGC (table 250.122). From Chapter 9, Table 8, one 2/0 conductors has a cross-sectional area of 133,100 circular mils; therefore, two 2/0 EGC's in parallel equals 266,200 circular mils, thereby satisfying the minimum requirement of 250,000 circula mils (250 kcmils). Remember, each EGC connected in parallel cannot be smaller than 1/0.(see exceptions).
 
Re: Parallel EGC

I?m not sure who I am disagreeing with here, but if I prove to be right, I prefer Maker?s Mark to a beer. ;)

I don?t think you can combine two or more conductors in parallel, to form a single EGC. As Ryan pointed out, 310.4 (2002 version) explicitly states that you can parallel a ?phase, neutral, or grounded? conductor. I am not sure why it says both ?neutral? and ?grounded,? as I thought these terms to be synonymous. But EGC is very conspicuous in its non-inclusion in this list.

The next to last sentence of 310.4, as discussed above by Ryan and the other Charlie, does not, in my view, permit the use of a set of smaller, parallel, EGC conductors. It merely states that if you include an EGC in the raceway that contains the phase, neutral, or grounded conductors, then the EGC must be sized per 250.122. There is nothing in 250.122 that permits the use of a set of smaller, parallel, EGC conductors. What it requires is a full-sized EGC in each raceway.

I think the key words that I am interpreting differently than Ryan and Charlie are the words, ?Where (EGCs) are used with conductors in parallel. . . .? This is not the same as saying, ?Where parallel conductors are used to form an EGC.? Rather, I read this sentence as saying, ?Where a single, full-sized EGC is used with phase conductors that are installed as sets of paralleled conductors. . . .?
 
Re: Parallel EGC

I tend to agree with Charlie on this one. The wording seems reasonably clear that you cannot run multiple smaller EGCs to make an equivilant larger EGC as you can with actual current carrying conductors. The wording is somewhat obtuse though.

Maybe it just doesn't come up that often since the EGC is usually quite a bit smaller anyway.
 
Re: Parallel EGC

What words prohibit installing EGCs in parallel? The wording in 310.4 is only premissive. It clearly permits parlleling the ungrounded and grounded circuit conductors, but it does not prohibit the paralleling of the EGC.
Don
 
Re: Parallel EGC

I don't know.......This one says more than one:

250.119 (B) Multiconductor Cable. Where the conditions of maintenance and supervision ensure that only qualified persons service the installation, one or more insulated conductors in a multiconductor cable, at the time of installation, shall be permitted to be permanently identified as equipment grounding conductors at each end and at every point where the conductors are accessible by one of the following means:
(1) Stripping the insulation from the entire exposed length
(2) Coloring the exposed insulation green
(3) Marking the exposed insulation with green tape or green adhesive labels
 
Re: Parallel EGC

Originally posted by charlie: Don, I think the way the Code is worded, it is inferred.
I agree. Since they went out of their way to explicitly state that it is OK to parallel some conductors, and then gave specific rules and exceptions under which this is acceptable, I believe they did imply that an EGC should not be on the list. Or so I infer.

But here?s a new twist that just occurred to me. As I mentioned earlier, the list includes phase, neutral, and grounded. But I think the last two are the same thing. Could the code committee have meant phase, grounded, and EGC? Could this have been a typo?

Here?s another tidbit: The 1987 version just listed ?phase or neutral.? The 1990 version changed this to ?phase, neutral, or grounded.? I am no longer a member of the NFPA, so I can?t look into the basis for this code change. Anyone want to take on this task?
 
Re: Parallel EGC

It seems to me there is no prohibition on paraleling EGCs, which is in fact a common practice. There does not seem to be any allowance for using multiple smaller EGC in lieu of a larger EGC that might be required.

i.e. - you can't replace a single 500MCM EGC with (2) 250MCM.
 