It would depend on the total length of the conductors, a one foot difference in a ten foot parallel run is a lot different than one foot in a hundred foot run.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No parallel conductors are the same length, the requirement is not practicable. As Roger stated the overall length of the run is the critical factor. IMO the NEC should allow a tolerance like no more then X% difference between the parallel conductors to make it considerate of real world conditions.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
No parallel conductors are the same length, the requirement is not practicable. As Roger stated the overall length of the run is the critical factor. IMO the NEC should allow a tolerance like no more then X% difference between the parallel conductors to make it considerate of real world conditions.

:thumbsup:
 

Besoeker

Senior Member
Location
UK
No parallel conductors are the same length, the requirement is not practicable. As Roger stated the overall length of the run is the critical factor. IMO the NEC should allow a tolerance like no more then X% difference between the parallel conductors to make it considerate of real world conditions.
I agree - not practicable. An allowable tolerance would seem like a reasonable suggestion. But then how would/could that be checked/policed/inspected after installation?
 

Ingenieur

Senior Member
Location
Earth
I agree - not practicable. An allowable tolerance would seem like a reasonable suggestion. But then how would/could that be checked/policed/inspected after installation?

the method used to ensure they are exactly the same length?

if you have 500' run within 1' that is a violation?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I recently was at an existing service that had parallel 350's for neutrals. One was 6' long, the other 9' long.
Had 11A on one and 1A on the other.
 
I don't think the rule is followed much. Lay all your conductors out on the ground and cut to the same length then install. It won't look pretty. You can tell just by looking at an install if they were actually cut to the sam length.
 

Besoeker

Senior Member
Location
UK
the method used to ensure they are exactly the same length?

if you have 500' run within 1' that is a violation?
I don't know what your code would say about that.
How would you measure it to determine if it was a violation was my question.
 

Ingenieur

Senior Member
Location
Earth
I recently was at an existing service that had parallel 350's for neutrals. One was 6' long, the other 9' long.
Had 11A on one and 1A on the other.

there had to be something else going on
total i = 12
R = ohm/ft
current divider

one branch i = 12 x 6R/(15R) = 4.8
other i = 12 x 9R/(15R) = 7.2

length delta should have little to do with ph-ph sc i
La and Lb = length of faulted phases
i sc = v/((La + Lb) x R/ft)

obviously for a gnd fault the longer will be a bit lower
R = ph ohm/ft, Rg = egc ohm/ft
gnd Rg ~ 50% higher so = 1.5R
i gf a = (v/sqrt3)/((La + 1.5Lg) x R)
i gf b = (v/sqrt3)/((Lb + 1.5Lg) x R)
ratio i gf a/ingf b = (Lb + 1.5Lg)/(La + 1.5Lg)

as L>0 the limiting factorbis Lg
assume La = 10', Lb = 8' and Lg = 10'
i gf a= 23/25 x i gf b = 0.92 x i gf b
for a 20% ph L delta the shorter cond i gf will be 8% higher

as length >inf
assume 100' with La = 100, Lb = 90 and Lg = 100
i gf a= 240/250 x ib = 0.96 x i gf b
ia will be 4% lower or ib 4% greater for a ph L delta of 10%
 
Last edited:

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Even if you used precision techniques to make the cable lengths the same, you would still have production tolerance on the diameter of the conductors themselves.

But to answer the OP, different lengths would mean different impedance, which would mean that the fault current would be unevenly distributed between the conductors.

-Jon
 

Besoeker

Senior Member
Location
UK
Even if you used precision techniques to make the cable lengths the same, you would still have production tolerance on the diameter of the conductors themselves.

But to answer the OP, different lengths would mean different impedance, which would mean that the fault current would be unevenly distributed between the conductors.

-Jon
Yes. But unevenly enough to be a problem?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I recently was at an existing service that had parallel 350's for neutrals. One was 6' long, the other 9' long.
Had 11A on one and 1A on the other.
There was something in addition to the length difference at work there. Based on just the length, the 6' one should have 60% of the current and the 9' one should have 40% of the current.
(Sorry, Ingenieur, I posted without scrolling down and reading your post)
 

Ingenieur

Senior Member
Location
Earth
There was something in addition to the length difference at work there. Based on just the length, the 6' one should have 60% of the current and the 9' one should have 40% of the current.
(Sorry, Ingenieur, I posted without scrolling down and reading your post)

no need for aplogies
always good to confirm
thnx
 

Besoeker

Senior Member
Location
UK
there had to be something else going on
total i = 12
R = ohm/ft
current divider

one branch i = 12 x 6R/(15R) = 4.8
other i = 12 x 9R/(15R) = 7.2

length delta should have little to do with ph-ph sc i
La and Lb = length of faulted phases
i sc = v/((La + Lb) x R/ft)

obviously for a gnd fault the longer will be a bit lower
R = ph ohm/ft, Rg = egc ohm/ft
gnd Rg ~ 50% higher so = 1.5R
i gf a = (v/sqrt3)/((La + 1.5Lg) x R)
i gf b = (v/sqrt3)/((Lb + 1.5Lg) x R)
ratio i gf a/ingf b = (Lb + 1.5Lg)/(La + 1.5Lg)

as L>0 the limiting factorbis Lg
assume La = 10', Lb = 8' and Lg = 10'
i gf a= 23/25 x i gf b = 0.92 x i gf b
for a 20% ph L delta the shorter cond i gf will be 8% higher

as length >inf
assume 100' with La = 100, Lb = 90 and Lg = 100
i gf a= 240/250 x ib = 0.96 x i gf b
ia will be 4% lower or ib 4% greater for a ph L delta of 10%

Was that necessary?
Other than .........let's not go there
 