Not taking sides here however a detailed mathematical analysis of current flow is appreciated, it goes to the heart or intent of the code, if not the word of it.
As noted, conductors are rarely of exactly the same length... I would go so far as to say they are never exactly the same length in parallel installations. Also already as noted, there will be slight differences in current flow upon parallel conductors, which are more pronounced as the run gets shorter. To wit: a 30-foot run with two left or right hand sweeps in 4 inch conduit, with the conduits laid out in a 4 by 1 configuration, the inside conductors could be as much as 12ft shorter than those on the outside. This is a pretty extreme example, however it is something to think about when laying out conduit and using parallel conductors
As noted, conductors are rarely of exactly the same length... I would go so far as to say they are never exactly the same length in parallel installations. Also already as noted, there will be slight differences in current flow upon parallel conductors, which are more pronounced as the run gets shorter. To wit: a 30-foot run with two left or right hand sweeps in 4 inch conduit, with the conduits laid out in a 4 by 1 configuration, the inside conductors could be as much as 12ft shorter than those on the outside. This is a pretty extreme example, however it is something to think about when laying out conduit and using parallel conductors