I would like a little help on calculating parallel feeders.
Single family dwelling existing 200 amp service customer would like to move up to 400 amps.
Would I be better off staying with 400kcmil single conductor, Table 310.15(B)(6)or figure parallel runs?
How do I calculate the appropriate conductor for parallel runs?
Table 310.16 4/0 at 90deg. 260 * 80% = 208
Parallel 4/0 THWN/THHN in one 2 ?? conduit for 400 amps?
I look forward to your input.