ThorHs said:What is the purpose of Parallel Feeders and when and where shoud I use them
iwire said:A set of 600 Kcmil copper will provide 420 amps of capacity and is about as large a conductor as I want to have to handle, pull, terminate .....
Bill W said:That's correct if memory serves. Not sure about the non metallic though, as long as the conduits are very close together,
steve66 said:In general, you have to have all three phase conductors in each conduit (if there is a neutral and/or ground, they are also ran in each conduit).
However, I think there is an exception that lets you bundle each phase in a separate conduit for underground installations with non-metallic conduit.
I might also add that parallel conductors need to be the same size, type, and length. They are also ran in the same size and type of conduits. This all keeps the ampacity equal on each parallel run.
Steve