Need to install a 3000 amp feeder. Planning on using 500 MCM CU, (feeders spec'd CU). There is am exisitng 600 amp feeder along the exact same route made up of 350 MCM in 3" EMT. I plan on reusing those conduits and pulling out 350s and pulling in 500s and installing 6 more 3 1/2" conduits, larger size for ease of pulling in the wire.
Question is, conductors will be cut to same length to meet 310.4, but would the different sizes of EMT not meet the "raceway..same physical characterisitcs" requirements?
Question is, conductors will be cut to same length to meet 310.4, but would the different sizes of EMT not meet the "raceway..same physical characterisitcs" requirements?